I have two electrical outlets in a bedroom that are not working. When I open them up, the black wire tests hot and the white wire tests cold (neutral), (There's no green(ground) wire (old house) ) The black(hot) wire is connected to the copper side screws and the white(neutral) wire is connected to the silver screw side on the outlet. But, the outlet does not work. Bought a new outlet connected it and it still does not work. I've worked with electricity a lot, (even installed a main panel box), but this problem stumps me. Any ideas?
  • Topic Stats
  • Top Replies
  • Link to this Topic
Type: Question • Score: 2 • Views: 1,492 • Replies: 10
No top replies

 
Tes yeux noirs
 
  1  
Reply Sat 24 Oct, 2015 04:34 am
@pryan2,
Quote:
the white wire tests cold (neutral)

This means what? Not-hot?
pryan2
 
  1  
Reply Sat 24 Oct, 2015 05:47 am
@Tes yeux noirs,
Yes, not hot, no current,
Tes yeux noirs
 
  1  
Reply Sat 24 Oct, 2015 05:49 am
@pryan2,
Quote:
Yes, not hot, no current,

You need to understand that the test does not tell you whether it is a true supply neutral wire, or a disconnected wire.
dalehileman
 
  1  
Reply Sat 24 Oct, 2015 11:28 am
@pryan2,
Quote:
the black wire tests hot
Curious, Pry, how you determined this: I'm wondering whether you used a voltmeter or actually attached a load of some sort. In the former case a voltage reading (esp if slightly lower than expected) might signify capacitive coupling; in which case the application of even the slightest load will cause it to drop to zero
pryan2
 
  1  
Reply Fri 30 Oct, 2015 03:44 am
@Tes yeux noirs,
Very Interesting! How would/could I determine whether the neutral(white) wire is a true supply neutral? The white wire comes from the top of the outlet box, loops around the screw(silver) and returns upward (probably to the junction box in the ceiling light. The fuse box is nearby in the hall, but has many while wires on the bus. Thanks.
pryan2
 
  1  
Reply Fri 30 Oct, 2015 03:50 am
@dalehileman,
I'm using a Klein Tools voltage meter. Someone has suggested that the white wire might just be a dead(disconnected) wire and not a true return neutral. Does this sound feasible to you? How would I troubleshoot this? Thanks.
Tes yeux noirs
 
  1  
Reply Fri 30 Oct, 2015 04:33 am
@pryan2,
Quote:
Does this sound feasible to you?

Yes.

Quote:
How would I troubleshoot this?

Look for disconnected neutral at junction box on way to breaker box or at breaker box. Or get an electrician.
0 Replies
 
engineer
 
  2  
Reply Fri 30 Oct, 2015 07:30 am
@pryan2,
1) Kill the breaker and put a locking device on it
1a) Make sure the breaker is open
2) Have someone else make sure the breaker is open
3) Measure the voltage at the outlet to see that it is zero.
4) Tie the white and black wires together at the outlet
5) Measure the resistance at the breaker. It should be practically zero. If it is not, you have a break somewhere.
6) Untie the white and black wires.
Tes yeux noirs
 
  1  
Reply Fri 30 Oct, 2015 07:48 am
@engineer,
That's good.
0 Replies
 
dalehileman
 
  1  
Reply Fri 30 Oct, 2015 10:56 am
@pryan2,
Quote:
How would/could I determine whether the neutral(white) wire is a true supply neutral?
Pry that's really a good q. Assuming there's no additional malfunction to mess up our observations. set ohmmeter to low range to determine resistance between the questionable wire and the supposed neutral at another outlet. I'd expect to find it slightly lower than comparing it to "ground," usu green. However this might give misleading results in some areas, esp after rain so isn't conclusive

Another: Connecting voltmeter (again set at low range) between ground and the q conductor, introduce an ac current by applying a load of some sort. If there's a slight increase in the reading, then your q must truly be neutral not ground

But maybe the guys really good at electricity know an even easier way
0 Replies
 
 

Related Topics

Main Breaker Tripped 2x - Question by decadent
240 Why - Question by lenchase
electrical showers - Question by grains93
6000W cooktop circuit - Question by 1hairycanary
Tempory power supply - Question by 51 nelson
How does a transformer work? - Question by SuzaneK
 
  1. Forums
  2. » Electrical Outlet Not
Copyright © 2024 MadLab, LLC :: Terms of Service :: Privacy Policy :: Page generated in 0.03 seconds on 04/26/2024 at 04:47:45