Kitchen wiring

 
 
lesha22
 
Reply Thu 30 Apr, 2015 06:30 am
Anybody sees any issues with this plan??

1. 48" stove dedicated on 50amp/240v
2. main sink disposal (7amps) dedicated on 15amp
3. 7 GFCI outlets on a dedicated 20amp
4. under cabinet microwave on island (1000w,14.5amps) dedicated on 15amp
5. undercabinet lights (13 feet of rope light @12.2w/3.3ft = 48.06w) and recessed lights (12 led - 12w each = 144w) on 15amp == 192.1 TOTAL WATT)
6. island sink disposal (7amps) and 4-5 GFCI (on island) outlets on 20amp
7. 48" fridge (10amps) and 1 outlets (pantry room) and 1 GFCI in Kitchen on 20amp
8. 48" hood (9amps) and 8 inside cabinets lights (puck 4.4w each, 35.2w total) on 20amp
9. dishwasher (1300w, 12amps) dedicated on 15amp
  • Topic Stats
  • Top Replies
  • Link to this Topic
Type: Question • Score: 0 • Views: 616 • Replies: 1
No top replies

 
carloslebaron
 
  1  
Reply Mon 4 May, 2015 03:23 pm
@lesha22,
#3

There must be 2 (two) circuits for receptacles in kitchens.

This means, 4 receptacles in one circuit, 3 receptacles in another circuit or, two circuits running on the 7 receptacles.

GFI receptacles are required when close to the sink, and I don't think your kitchen sink is that long to connect 7 GFI receptacles close to it.

You can install the GFI receptacles over the counter close to the sink, the rest can be regular receptacles. You are not adding more safety or anything similar by using GFIreceptacles when not required by code.

But, it's your money.

Enjoy your kitchen.
0 Replies
 
 

Related Topics

Poo-tee-weet? - Question by boomerang
Let's just rename them "Rapeublicans" - Discussion by DrewDad
Which wood laminate flooring? - Question by Buffalo
Lifesource Water versus a 'salt' system - Discussion by USBound
Rainsoft - Discussion by richb1
Crack in Ceiling - Question by Sam29288349
 
  1. Forums
  2. » Kitchen wiring
Copyright © 2025 MadLab, LLC :: Terms of Service :: Privacy Policy :: Page generated in 3.13 seconds on 01/06/2025 at 04:35:23