Do you need to use hospital grade mc in veterinary facility
  • Topic Stats
  • Top Replies
  • Link to this Topic
Type: Question • Score: 3 • Views: 932 • Replies: 4
No top replies

 
Butrflynet
 
  2  
Reply Thu 19 Mar, 2015 07:35 pm
@bmacfadden88,
MC what? MC Hammer?
bmacfadden88
 
  1  
Reply Thu 19 Mar, 2015 07:39 pm
@Butrflynet,
Metallic cable
0 Replies
 
bahtah
 
  2  
Reply Fri 20 Mar, 2015 08:09 pm
@bmacfadden88,
If you are considering this to meet a Health Care Facility requirement the answer is no. Article 517 is applicable to Human beings only not animals. That being said there would be GFCI requirements and grounding requirements depending on what type of animals are being treated and how they are housed. Article 547 may be of interest especially Equipotential Planes.
0 Replies
 
RayEGarcia
 
  1  
Reply Mon 23 Mar, 2015 12:04 am
I never heard about MC in veterinary field. Can you explain in brief what you want to say about MC??
0 Replies
 
 