Neon light doesn't go off on an British General 45A 1-Gang Double Pole Cooker Switch

 
 
Reply Thu 15 Jan, 2015 03:11 am
I have fitted a new switch and although the switch works, the neon light doesn't go off when the switch is switched off. Any advice?
  • Topic Stats
  • Top Replies
  • Link to this Topic
Type: Question • Score: 0 • Views: 753 • Replies: 3
No top replies

 
contrex
 
  1  
Reply Thu 15 Jan, 2015 10:42 am
@HaloWill,
Quote:
Any advice?

Check switch is wired correctly.
0 Replies
 
contrex
 
  2  
Reply Thu 15 Jan, 2015 04:04 pm
You have probably wired the load and feed the wrong way round, so that the neon is permanently across the supply side. Therefore the switch cannot isolate it - but it can still isolate the cooker because when the switch is OFF the circuit through it to the cooker is still broken.

You must rewire the switch and take care to connect the supply and load wires to the right terminals. These will be labelled - probably something like L in, N in, L out and N out; or L sup, N sup, L load, N load.

Don't forget to connect the earth wires properly.
HaloWill
 
  1  
Reply Fri 16 Jan, 2015 07:34 am
@contrex,
That's done the trick. Thanks very much.
0 Replies
 
 

Related Topics

Electrical transformer question - Question by boomerang
How to disguise my ugly light fixtures? - Question by boomerang
Recess floor lighting - Question by Timberr
Dimmable Ballast Problem - Question by Aubatron
Lightbulb stuck or twisted in socket - Question by kellabella83
Li'l blinkin' red light - Question by dalehileman
 
  1. Forums
  2. » Neon light doesn't go off on an British General 45A 1-Gang Double Pole Cooker Switch
Copyright © 2024 MadLab, LLC :: Terms of Service :: Privacy Policy :: Page generated in 0.03 seconds on 05/03/2024 at 01:42:44