Subpanel Breaker Size

 
 
briding
 
Reply Mon 15 Dec, 2014 10:48 am
I am adding a new addition to a house. 28 x 24. I will have 5 light switches, 16 lights, & 30 outlets. 2 will be for TV's. Can someone tell me what size circuit breaker I will need for this. I will be running a subpanel that is separate from the main subpanel. The meter is about 100' away from the house and addition. The house is running off a 55 amp breaker. The main service panel is a 200 amp. Any help would be appreciated.
  • Topic Stats
  • Top Replies
  • Link to this Topic
Type: Question • Score: 3 • Views: 659 • Replies: 1
No top replies

 
bahtah
 
  1  
Reply Mon 15 Dec, 2014 05:04 pm
@briding,
I am curious as what the room is going to be used for. You have about 100ft of wall and 30 receptacles, seems like over kill. Also a 672sqft room with 16 lights.
What is the wattage of the fixtures you plan to use. Even if you took all the lights at 100watts each and the receptacles at 180watts (neither is a residential code load requirement), you would have about 7000 watts/240=29.16 amps. Not knowing more about the room I doubt you would even have that much load. Based on what you listed a 30amp circuit to a small panel would be enough. At 100ft even if you had a full load of 30amps, the voltage drop would only be slightly over 3% and I doubt you will ever see full load on the circuit.
0 Replies
 
 

Related Topics

Main Breaker Tripped 2x - Question by decadent
240 Why - Question by lenchase
electrical showers - Question by grains93
6000W cooktop circuit - Question by 1hairycanary
Tempory power supply - Question by 51 nelson
How does a transformer work? - Question by SuzaneK
 
  1. Forums
  2. » Subpanel Breaker Size
Copyright © 2024 MadLab, LLC :: Terms of Service :: Privacy Policy :: Page generated in 0.06 seconds on 12/22/2024 at 08:20:06