You have a kiln + fans drawing 75 amps. Plus whatever else is running off of the garage system (lights, etc...). It is possible that you reached the magic 100 amp tipping point. That 70 amp draw for the kiln may be it's "normal" operating current. It might surge a little higher at times.
The 100 Amp breaker in your garage sub-panel is ONLY for your kiln. The 100 breaker in your main panel is for everything in your garage. So what else is running in your garage? Lights? Garage door opener? Appliances? Radio? Pottery wheel?
Also. check your breakers. You may find the kiln breaker in the sub-panel in the garage is a delayed-action breaker and the one in the main panel in the house isn't.