range hood

 
 
Reply Sat 28 Jun, 2014 11:31 am
range hood light and fan quit working checked voltedge and it only drawing 90 volts and is hard wired in ......every other thing on same circute is at 120.........if I just dont use the range hood do I have anything to worry about
  • Topic Stats
  • Top Replies
  • Link to this Topic
Type: Question • Score: 0 • Views: 881 • Replies: 10
No top replies

 
Ragman
 
  1  
Reply Sat 28 Jun, 2014 11:56 am
@bemabound,
Well that would depend on if there's something causing it to short out or partially short out. Do you feel heat anywhere...being generated..or is their a smell of smoke? Why not just replace the fan motor and/or replace the wiring?
dalehileman
 
  1  
Reply Sat 28 Jun, 2014 01:15 pm
@bemabound,
Does the voltage jump to 120 when you turn 'em off

Or Bema, by "hard wired" do you mean there's no switch that wold let you do so

Or by "…use range hood…" do you mean it's somehow disconnected when not in use
bemabound
 
  1  
Reply Sat 28 Jun, 2014 01:21 pm
@Ragman,
no smell of smoke and what wire I can feel is fine I do plan on rewiring but the attic here is well over 100 degrees in the summer and want to wait till the fall
0 Replies
 
bemabound
 
  1  
Reply Sat 28 Jun, 2014 01:25 pm
@dalehileman,
90 volts is the what the main wires read on the meter the only on off switches are the ones for the light or fan
dalehileman
 
  1  
Reply Sat 28 Jun, 2014 02:53 pm
@bemabound,
Sorry Bema if I seem dense but you've made ref to "...every other thing…" being at 120 v so by "main wires" at 90 v I assume you mean those leading to the hood. I also assume that light and fan must be the only loads on the hood. So what voltage do get with just the fan off? or just the light? or both?
bahtah
 
  2  
Reply Sat 28 Jun, 2014 03:02 pm
@bemabound,
The range hood should have an accessible junction box. Disconnect the circuit from the hood and then take your voltage reading. If you then read 120V as you should, the problem is in the hood and not in the attic. If you do not want to fix the hood now, leave it disconnected and cap off the wires.
bemabound
 
  1  
Reply Sun 29 Jun, 2014 09:11 am
@dalehileman,
sorry it took so long to get back to ya every other thing refers to those on the same circut breaker at 120v just the wires that feed the hood range are at 90v
bemabound
 
  1  
Reply Sun 29 Jun, 2014 09:16 am
@bahtah,
sorry it took so long........I did access the junction box and it is there that the 90v occures in the lead wires from the circut breaker every thing else on that circut breaker reads 120v
dalehileman
 
  1  
Reply Sun 29 Jun, 2014 10:45 am
@bemabound,
Okay Bema the problem is clearer. Poke around with your voltmeter to find that missing 30v. There might be for instance (1) a miswiring that places an intervening load in series with the hood hot wire or (2) more likely an open circuit in neutral that connects the hood return instead to earth ground

Very, very unlikely the wiring is okay but (3) you'll find this 30v divided between the two. That is for instance 15 v from main hot to hood hot and 15 v between main return and hood return, caused typically by a short in the motor. In this case however one would expect wires to the hood getting very hot






0 Replies
 
bahtah
 
  1  
Reply Sun 29 Jun, 2014 06:43 pm
@bemabound,
Quote:
sorry it took so long........I did access the junction box and it is there that the 90v occures in the lead wires from the circut breaker every thing else on that circut breaker reads 120v

Did you disconnect the wires to the hood and then take your reading?
What else is on that circuit?
0 Replies
 
 

Related Topics

Main Breaker Tripped 2x - Question by decadent
240 Why - Question by lenchase
electrical showers - Question by grains93
6000W cooktop circuit - Question by 1hairycanary
Tempory power supply - Question by 51 nelson
How does a transformer work? - Question by SuzaneK
 
  1. Forums
  2. » range hood
Copyright © 2024 MadLab, LLC :: Terms of Service :: Privacy Policy :: Page generated in 0.03 seconds on 05/02/2024 at 06:51:07