Reply Mon 23 Jun, 2014 06:51 pm
I have a residential property that has a voltage drop issue. When the utility power is on and all breakers in the panel are OFF, the voltage reads 120 to ground and 240 phase to phase. As you start to turn breakers on the A phase voltage begins to drop. By the time all of the breakers are on the A phase only reads 45 volts and the phase to phase reads 120v.....has anyone ever seen anything like this before? The utility and the underground service has been tested and reads out fine. It has to be something in the panel board or even somewhere in the house. Any ideas would be appreciated.
  • Topic Stats
  • Top Replies
  • Link to this Topic
Type: Question • Score: 0 • Views: 1,222 • Replies: 2
No top replies

 
bahtah
 
  1  
Reply Thu 26 Jun, 2014 03:37 pm
@belectric,
Usually unbalanced voltage is caused by an open neutral. You need to take your readings from phase to neutral. Did the utility pull the meter and check the meter socket? A little more info would be helpful. Are the breakers in the same panel as the service disconnect or a sub-panel?
0 Replies
 
dalehileman
 
  1  
Reply Thu 26 Jun, 2014 04:16 pm
@belectric,
Bah's response very logical. Get a voltmeter; measure between neutral and some known ground such as a water pipe. More than a few volts confirms Bah


On the other hand it's also possible that an open circuit or wiring error somewhere has placed an appliance or other load in series with your box
0 Replies
 
 

Related Topics

Main Breaker Tripped 2x - Question by decadent
240 Why - Question by lenchase
electrical showers - Question by grains93
6000W cooktop circuit - Question by 1hairycanary
Tempory power supply - Question by 51 nelson
How does a transformer work? - Question by SuzaneK
 
  1. Forums
  2. » Voltage Drop Issue
Copyright © 2024 MadLab, LLC :: Terms of Service :: Privacy Policy :: Page generated in 4.75 seconds on 12/26/2024 at 05:16:46