@dalehileman,
dalehileman wrote:I had noted in my youth this happens sometimes if for instance the transformer ("receiver")' is of heavier duty than required
Yes. When any transformer is connected to the supply there is what is called an 'inrush' current lasting several cycles of the AC waveform. This is because the iron core of the transformer needs to get magnetised. Inrush current is also sometimes known as surge current, and is
always higher than the normal operating current of the equipment. It can be between 5 to 100 times greater.
Quote:However it might also be that you had simply forgotten that the step-up doubles the load you might have expected according to the freezer's rating
He has a 220 V refrigerator; he must therefore (assuming a domestic supply) be stepping up from 110 V; the refrigerator is rated 123 W (constant rating) which gives a secondary current of around 1.8 A and a primary current of 3.6 A (we will ignore power factor although fridges do have motors).
A fuse's marked rating in amps is the current that it will carry indefinitely without blowing; if that current is exceeded then the fuse should melt after some time. Whether it just quietly gives up the ghost after some seconds or minutes or goes out with a BANG as soon as you throw the switch depends on the the size of the overload.
Sometimes a fuse of higher rating and/or a slow-blow type may help with inrush surges drawn by transformers, and as you note, Dale, a 500 VA device is getting a bit big for a domestic setting without any special arrangements such as these.
Bottom line SPEAK TO AN ELECTRICIAN. Monkeying about with circuit protection can result in fires or damage.
Quote:You might cite some figures
E.g. the rating of the fuse that blows.