Electrical Wiring Circuit - 1 Dimmer, 6 Pot Lights(outdoor), 2 plugs (outdoor)

 
 
Reply Sat 28 Sep, 2013 10:42 pm
I am running a circuit and having some issues.

Circuit Contains:
- 1 Dimmer Switch feeding 6 pot lights
- 2 Plugs

The power is coming from the breaker box to the switch box.
The switch box has lines out to the first outdoor outlet and one light

In the switch box I have performed the following connections:
- all white wires are connected
- all ground wires are connected and connected to the box and the dimmer switch
- the hot black is connected with the black to the plug and one black on the dimmer switch
- the other black on the dimmer switch is connected to the black leading to the pot light


For the first plug I have a GFIC plug because it is outside.

This issue I am having is as follows:
When I have the lights hooked up and the GFIC plug wired bring the hot into it and nothing going out everything works fine. However, when I attached the line to the next plug the GFIC will no longer reset. If I move the GFIC from the first plug to the last plug everything works fine but I then have one outdoor plug unprotected by the GFIC plug.

I have tried 2 separate GFIC plugs to ensure I don't have a faulty plug but I continue to have the same issue.

What am I missing here?
  • Topic Stats
  • Top Replies
  • Link to this Topic
Type: Question • Score: 2 • Views: 1,662 • Replies: 2
No top replies

 
Ragman
 
  1  
Reply Sun 29 Sep, 2013 12:23 am
@cdjordan,
Quote:
What am I missing here?


An electrician
0 Replies
 
bahtah
 
  1  
Reply Sun 29 Sep, 2013 11:52 am
@cdjordan,
Sounds like you may have used the grounded circuit conductor from the feed-thru side of your GFI receptacle to supply your light. If your first GFCI is protecting your second receptacle, it will be feed from the load side of the first GFCI receptacle. If you connected your light to the grounded circuit conductor on the load side of the first GFCI it will create an imbalance that will trip your first GFCI because it will no longer see a balanced circuit. I am not sure if that is what you did as I do not know what conductors you installed where but that's my best guess at this point. If that is what you did, then just tap off on the line side of the GFCI for the light.
0 Replies
 
 

Related Topics

Poo-tee-weet? - Question by boomerang
Let's just rename them "Rapeublicans" - Discussion by DrewDad
Which wood laminate flooring? - Question by Buffalo
Lifesource Water versus a 'salt' system - Discussion by USBound
Rainsoft - Discussion by richb1
Crack in Ceiling - Question by Sam29288349
 
  1. Forums
  2. » Electrical Wiring Circuit - 1 Dimmer, 6 Pot Lights(outdoor), 2 plugs (outdoor)
Copyright © 2025 MadLab, LLC :: Terms of Service :: Privacy Policy :: Page generated in 0.03 seconds on 02/05/2025 at 12:54:56