1
   

VFD to a pump

 
 
BrettB
 
Reply Thu 20 Oct, 2016 11:35 am
i have a VFD that will only shut the pump down to 4%(4hz) when controlled from the control room. when i go to the VFD itself and push the stop button it will finish shutting down all the way. what could be causing this problem?
  • Topic Stats
  • Top Replies
  • Link to this Topic
Type: Question • Score: 1 • Views: 246 • Replies: 6
No top replies

 
dalehileman
 
  1  
Reply Thu 20 Oct, 2016 12:05 pm
@BrettB,
Brett, miswiring

Forgive

VFD = Very Fine Device
0 Replies
 
contrex
 
  1  
Reply Thu 20 Oct, 2016 12:29 pm
Variable Frequency Drive used to control speed of AC motor. Not all of them can run down to zero RPM.
BrettB
 
  1  
Reply Thu 20 Oct, 2016 12:44 pm
i found the issue it was still giving the vfd the run command when we tried to stop it so its a plc/sequencing issue
0 Replies
 
dalehileman
 
  1  
Reply Thu 20 Oct, 2016 12:45 pm
@contrex,
Aha thanks Con. Do you suppose it isn't really a problem, that's the way it's s'posed to work
BrettB
 
  1  
Reply Thu 20 Oct, 2016 12:47 pm
@dalehileman,
yes im sure i got on the phone with a technician from the manufacturer and we ran through the steps together and the code that its throwing is 0010HEX which means its still receiving a start signal.
dalehileman
 
  1  
Reply Thu 20 Oct, 2016 12:54 pm
@BrettB,
Interesting Brett you should so report as we've been experiencing troubles with our internet interplay, my BH on the 'fone with mfr for what seems like hours now

Mine works now but hers doesn't, some sort of interruption 'tween. Meantime I've suggested she try shutting power off then back on; you might try that too
0 Replies
 
 

 