@kevo84,
Ok, this is good information. Just to be clear:
- All the outlets on the breaker are dead.
- The breaker is closed and the outlet measures 125V
- You've replaced the outlet that got wet.
- There is no apparent GFI on this loop.
It is very unlikely that a GFI outlet would be in the attic, but there could be one in the garage. Where in your house is the outlet located? Are all the dead outlets in the same room, or are some in other rooms? There should be a GFI in each bathroom, the kitchen and on any outside outlets you have. It should be a two minute test to hit them all and reset them just to be sure. If your issue is in a bedroom, there might not be a GFI.
The next step is a little tedious. Kill the power and physically disconnect half the outlets (including the one you are worried about) then power back up. Do the other ones have power? If so, kill power, add half out the disconnected outlets back in and repeat. See if you can isolate it to one circuit.