Reply
Thu 29 Sep, 2016 11:49 am
I have 3 1KVA Transformers. Acme T 2 53010 S model. I want to transform 240V 3 phase to 480V Three phase. I wired each transformer as 240/480, and then connected them as a delta wye with the 240 side as the delta and the 480 sides as the wye, grounded in the center. I ended up with 1,000 volts on the output. I rewired ea transformer as 240/240, delta wye and ended up with 440V on the output. I can drive a 3 phase 480V motor with it, but I would really like to have 480V.
Any idea what I am doing wrong? Was I wrong to assume I could use 3 480/240 transformers, with the 240v inputs used to get 480V out in a delta wye configuration.
To be specific on the transformer wiring, I connected h2 to h3 on each transformer. X2 to X3. Wired the H1 H4's in a wye. Wired the X1 X4's as a delta. Then put 240V 3 phase on the x side.
@shelato,
Shel a schematic might be helpful
@shelato,
With such a system, you cannot have a three phase, 480 V between phases.
You would need three transformers with a 277 V primary in order to obtain 480 V on a three phase secondary.
The resulting ratio is given by multiplying your primary voltage by square root of 3.
@timur,
Ugh! Yes I understand. I don't know why I missed that. I found 3 240/277 transformers and will start over.